Jea48, please find the technical data to back up your statement. Dont just disagree , prove your statement
- ...
- 43 posts total
>>"Jea48, please find the technical data to back up your statement. Dont just disagree , prove your statement"<< [Mapleleafs3] >>>>>>>>>> This may be on a grand scale but you will get the idea... http://205.243.100.155/frames/longarc.htm ======== |
One of the tests is the drop test. It goes something like this. The outlet is mounted 50 inches from the floor. A 3 foot cord with a hospital grade male cord cap and a 8 pound weight at the end of the cord is plugged into the hospital grade outlet. The weight is dropped straight down at the outlet height. The cord must stay plugged in and no damage done to the outlet to pass the test for hospital grade. |
Mapleleafs3 and Jea48 It should be noted that a loose electrical contact can and will heat up. This is where the fire hazard exists. The extra resistance will create hotter temperatures. They will also spark. So, no loose contacts so that sensitive equipment does not loose power (so many busy feet in a hospital) but also to avoid hotter than normal temperatures at the plug and in the receptacle. |