I agree with all of the excellent cautionary statements that have been made. I want to clarify that the suggestions in my previous post (the third post in this thread) did not mean to suggest anything contrary to these cautions.
I assume that there is and will continue to be a bond between ac neutral, safety ground, and earth ground at the main entrance of power into the house, near the breaker panel. For all existing runs, and for the new ones that may be added. The earth ground is essential for lightning protection, and the bonding of ac neutral and safety ground at that physical location is essential for effective circuit breaker operation, as the paper Jea48 linked to makes clear. And, yes, it seems likely that not having outlet receptacles may be a code violation.
But to restate the point I was trying to make: The downside of having dedicated runs to different parts of the system is increased voltage differential between the chassis of the different components, particularly at high frequencies, which can result in noise currents flowing through the same cable shields as signal return currents, thereby effectively summing the noise into the signal (the very thing that having multiple ac runs is intended to improve).
Connecting the grounds of the different runs together, near the system, will minimize those voltage differences. Jea may very well be correct that tying that local system ground to an earth rod will not accomplish anything, but I don't envision that it would have any negative effects either (in terms of either safety or performance).
A better approach all around, though, may be to utilize isolation transformers, as described by Zargon in this thread:
http://forum.audiogon.com/cgi-bin/fr.pl?htech&1228780109
Regards,
-- Al
I assume that there is and will continue to be a bond between ac neutral, safety ground, and earth ground at the main entrance of power into the house, near the breaker panel. For all existing runs, and for the new ones that may be added. The earth ground is essential for lightning protection, and the bonding of ac neutral and safety ground at that physical location is essential for effective circuit breaker operation, as the paper Jea48 linked to makes clear. And, yes, it seems likely that not having outlet receptacles may be a code violation.
But to restate the point I was trying to make: The downside of having dedicated runs to different parts of the system is increased voltage differential between the chassis of the different components, particularly at high frequencies, which can result in noise currents flowing through the same cable shields as signal return currents, thereby effectively summing the noise into the signal (the very thing that having multiple ac runs is intended to improve).
Connecting the grounds of the different runs together, near the system, will minimize those voltage differences. Jea may very well be correct that tying that local system ground to an earth rod will not accomplish anything, but I don't envision that it would have any negative effects either (in terms of either safety or performance).
A better approach all around, though, may be to utilize isolation transformers, as described by Zargon in this thread: