On one leg or two legs?


If you install two dedication circuits, would you install both breakers on the same leg or one on each? and why?
houstonreef
Are they on the same leg of the main power....(i.e. did you skip a breaker when you installed your new wire?

Why did you share the ground...that's something that only electricians use to save money on cable and to avoid having to pull multiple cables. Sharing the ground is OK (you want all the grounds coming to an outlet box to be grounded at the outlet box, but you should be running separate neutrals for each line back to the main power distribution box.
01-22-09: Ghstudio
Are they on the same leg of the main power....(i.e. did you skip a breaker when you installed your new wire?
Ghstudio,
You need to reread Houstonreef's post.....
Because of the wiring configuration he chose he has to have each hot wire, of the multi wire branch circuit, on opposite legs. Both hots share the same neutral, the two hots have to be fed from opposite legs. It's the nature of the beast....

01-22-09: Houstonreef
I used two wires for hot on each receptacle and share the ground and neutral.

I then installed two breakers on each leg of the panel.
=====================
01-22-09: Houstonreef
I installed the wire bought at Home Depot and it is CAROL Brand. it has four stranded 10 awg conductors, and very flexible.

Houstonreef,
Does the wire you bought look like
this
?
.
Jea48,

Yes, That is the wire.

I think i have to hire an electrictian to redo the whole thing. What kind of wire do you recommend?
EG., see my post above for starters.

Are or is this cable using twisted pairs?? In essence, did you simply run one cables then to use as a dedicated line for such a circuit? Did you keep the positive (hots) still twisted together? Same for the Neutral and ground, were they twisted together?

You should have put another neutral in there as you went with using two different phases. Albeit, things should work anyhow.

I’ve seen worse BTW.

If so the buzzing issue you experience without the use of the conditioner is due to some ground loop issue somewhere in the house. Plain and simple.

Keeping the pairs twisted together at first made me think you’ve added some inductance along the way too that would not ordinarily be there usually. But that’s not the deal.

As you ran two twisted pairs of #10 AWG stranded the wire alone should stand up to 30 A. Solid #10 = 25A max. Stranded #12 = 25A., and solid #12 = 20A max. the thinking behind why use the appropriate gauge wire is this, heat as well is a factor which increases current. An appropriately sized conductor will transmit and conduct that heat energy sooner than will larger gauge conductors.

…and that’s what we are trying to prevent here with proper ckt applications… fire, not necessarily saving the causer of the overload, but the rest of the array and perhaps lives.

Had you ran two runs of grounds and commons, I think it would have been more to code and better overall… at least in my area, that’s code.

In effect you have ONE dedicated line attached to two breakers for all intents and purposes, and again, it should work… but it’s the ‘cheapie/temp’ way to do things… and it pays to do electrical things properly.

To find the issue, turn off everything BUT the breaker controlling the thing that’s buzzing. Turn on the thing. See if it still buzzes.

If so it’s a ground loop… and likely comes from either your Pay TV svc. Or your phone svc.

If it doesn’t buzz while it’s the only energized thing in the house, begin flipping on breakers on that phase, one at a time… continue to the opposite phase, until you find the ckt to which the ground can be attributed.

Worse case scenario would be the ground issue is an accumulation of household items being used in which case l3eaving on the amp, and energizing more breakers/circuits will increase the level of the hum/buzz as you go along.

The choices once the item causing the issue is found are:

Call an electrician.

Disconnect things from the ckt which is causing the GL until you get to the actual culprit and never use that again. Cell phone charger, UPS for the PC, rheostat (lighting dimmer) , etc. or get a better one.

If the buzz is there with everything else off, it is most likely the cable TV or phone… to make sure, disconnect the coax feeding the Sat/cable box and see if you still have the buzz/hum.

In that case a transformer can be put inline with the coax feeding the cable box. Sometimes right at the box, or outside the house where the coax run begins.

If it’s the phone install another ground rod explicitly for the phone. I won’t guarantee this move, but I’ve seen it work. Disconnect the orig ground ckt, and drop the new rod several feet away from the orig one. 10 ft. should do.

Lift the ground from the receptacle the amp is plugged into. Either by a cheater plug (both hot & common but no ground pin), or by removing it from inside the outlet itself.

If you chose to put breakers one on each phase because that was the only available unused slots. There is a work around for that as well.

They are called Wafer breakers. Half the size of standard breakers so that two fit into the same space as ONE regular breaker. They come in various ampere & voltage sizes too. Thus allowing you to put both ded lines onto one phase, which was recommended.

I must also say here at this point, I was an electrician in my past. Mainly industrial and commercial efforts… some residential now and then on the side. I gotta say here you really should contact a card carrying sparky for this event, but if you feel compelled to proceed, it is surely at your own risk.

Not trying to scare ya… I’M just CMA.

Good luck. Hope that helps.