01-23-09: Houstonreef
Yes, That is the wire.
Houstonreef,
You cannot use portable Cord for fixed branch circuit wiring.... It is not approved by UL or NEC for such use.
01-23-09: Houstonreef
What kind of wire do you recommend?
It all depends on your circumstances as well as what your local governing authority allows. The electrician will advice you what will meet the code in your area.
If allowed for your wiring situation my first choice would be NM-B cable. I would also use plastic rough-in boxes.
Second choice would be MC cable with aluminum armor.
At any rate tell the electrician you want 120V dedicated branch circuits.
Dedicated branch circuit?
A 120V branch circuit that consists of;
(1) hot conductor
(1) neutral conductor
(1) safety equipment grounding conductor.
Make sure each dedicated branch circuit has its own NM-B cable or MC cable.
Do not combine dedicated circuits in the same cable or raceway, (conduit).
Tell him you want solid core copper wire #12 awg minimum. If the branch circuits are long move up to #10 awg solid copper wire.
And for the reasons Gs5556 pointed out in his post the length of the dedicated branch circuits should be the same. At least as close as possible in length.
Terminate both dedicated branch circuits on the same leg in the electrical panel.