new measurements:
L amp:
Correct cheater plug 62.5 V.
Reversed 51 V.
R amp:
Correct 62.5 V.
Reversed 51 V.
01-31-09: Maril555
Wow, I could see where the reading might be high in one direction, but not high in both directions.
I just checked my little ARC VT 50 power amp.
Correct plug orientation with the ground lifted was 3.6Vac
When I reversed the cheater in the receptacle outlet the voltage jumped up to 93.5Vac......
=================================
Would you do me a favor and conduct another small test for me?
Set you meter on the 250Vac scale.
Use the receptacle you were using for your test.
Insert one probe in the T slot, (neutral), of the recept and the other probe in the equipment ground making sure of a good mechanical contact.
Any voltage reading? It should be zero.
If no voltage, set the meter on the 50Vac scale and repeat the same test.
Any voltage reading? Again it should be zero.
Move the meter selector down to the next lower scale and repeat. The meter should still measure zero Vac.
One final test.
Set the meter on the 250Vac scale.
Measure the voltage between the Hot contact, small slot, and the neutral, T slot. Make note of the reading.
Next measure the voltage from the Hot contact to the equipment hole contact. Both voltage readings should be the same.
.