You misunderstood what I wanted you to do. All the test measurements are taken at the wall receptacle outlet only. No audio equipment is involved with the test.
In simple terms the test will tell if there is a good electrical continuity between the main incoming service neutral conductor, of your electrical service, and the equipment ground. At some point the electrical service entrance neutral conductor is connected to earth and is also bonded, connected, to the main equipment enclosure as well as equipment grounding bus bar/s. In most cases this is done at the main service electrical panel. Not sure in your case though. I noticed from your pictures the main breaker is not in the main panel so it is more than likely out side by the electric meter. Connection to earth and equipment bonding may have been done there.
So the test is a simple way to look at the thing just from one branch circuit and receptacle.
I tried to explain best I can in layman terms.
So at the wall receptacle outlet only.
Measure from the neutral to the equipment ground, (U shape hole).... Should show 0 volts
Measure from the hot to the neutral.... Should be around 120V to 123V
Measure from the hot to the equipment ground, (U shape hole)... Should be the same as the voltage measurement from Hot to neutral.
And one more measurement if you would. Plug in and turn on one of the power amps and using the other receptacle of the duplex receptacle measure the voltage from the hot to the neutral. This will give a somewhat load condition on the branch circuit for any voltage drop. The voltage should be within about one volt of the reading with the power amp not connected and turned on.
A true test would be to play some music at a moderate level and take the measurement.