Undertow,
128V is pretty high. You must go through a lot of burned out light bulbs.
Are you sure the volt meter you are using is giving you a correct reading of the voltage? Is the meter displaying true RMS or peak?
I am looking to keep the system self contained and moveable vs. hardwired built in. I will have to take advantage of existing circuits for the time being. it
Undertow 06-02-09:
You still could get by using one main isolation transformer and a small panel. Especially if your main electrical panel is in a basement and is exposed and easy to connect to.
Of course you will need to hire an electrician to do the job.
Install the transformer and new panel close to the existing panel. The electrician can easily move the existing audio branch circuits to the new panel.
I would suggest buying a transformer with a 240V primary and 120V secondary. You may have to get one with a 120/240V secondary and just parallel the two secondary windings, 120V out.
Here is the kicker though... You will need one more smaller transformer. This transformer will be a buck transformer connected between your main electrical panel and the primary winding of the main iso transformer. The buck transformer, (configured as an
autotransformer), will lower your now 256V mains down to 240V.
Balanced / isolation transformer
It will have about a 5% loss bringing my wild voltage down to about 122, and in theory in turn give me 61 volts per phase on the output plenty low enough now being split into a balanced load for any gear to run much more optimally for the most part. Nothing fancy, nothing current limiting or adjustable just one continous clean output more or less regardless what the wall is doing, each leg will not vary much more than between 58 to 64 volts.........
5% loss? Please explain the 5% loss.
NEC 2005 Code Article 647. Same for 2008.
http://www.equitech.com/support/647.htmlNote, the neutral is connected to ground. The 120V out for power use is two ungrounded hot conductors.
.