One question I haven’t nailed down as yet: Do I need to buy both a 100 amp (or, perhaps the 60-70 amp you mentioned) breaker for one of the two available slots on the main panel AS WELL AS a 100 Amp main breaker at the sub panel?
The sub panel does not need a main breaker. Buy a main lug only load center.
BTW, thank you for your tip about making all the wiring for the circuits off the subpanel the same AWG. I had thought about using 10/2 for the mono amp circuits and 12/2 for the rest. Your advice about not using a mixture of AWG is appreciated.
That was someone else but I agree..... As short as your branch circuit runs are you could use 12-2 W/G for all the branch circuits.The electrician would probably give you a big hug as well....
8' to 20' branch circuit runs, call me cautious but I would try to keep them with in a couple of feet of each other. No coiling up though...
A couple of final questions if you don’t mind…with a 100 amp subpanel in mind, the electrician had recommended a #3 AWG copper cable for the feeder line. I assume this means a 3 conductor solid core cable with safety ground wire…right?
Per UL for sizing the over current device,(breaker), for #2 awg wire and smaller use the
60* C column. #3 awg THHN/THWN copper wire is good for 85 amps.
If you look inside your 200 amp panel some where on the side you will see an info label. The label will say what the maximum allowable size branch circuit breaker that can be installed in the panel. Just guessing 80 amp. Check your panel.
In most cases the lug size on a 60 amp breaker is for a maximum size wire of #4 awg. You would have to use at least a 70 amp breaker for #3 awg wire. The maximum lug size for a 70, I believe, is #2 awg.
#3 awg wire will be stranded.
As far as trying to keep everything in the sub panel on the same leg is concerned…since it is being fed from only one leg off the main panel, does this mean that each and every breaker row in the sub panel is therefore also on this same leg? In other words, there’s no need to skip breaker rows in the sub to ensure the all the audio gear is fed from the same leg?
Are you feeding the sub panel with 120V only or 120/240V?
If 120/240V every other breaker down each side is the same Line, leg.
Future? I would probably feed the panel 120/240V
2 hots, 1 neutral, 1 equipment grounding conductor.
Jim