Unfortunately, I think your opinion lines up with mine and gives me reason to believe that a multiple circuit (dedicated or not) might cause more issues than it would solve.
BTW, I noticed your comments were specific to equipment connected via IC's. What about the notion that in a metal rack, ALL the equipment loaded into it is interconnected...whether interconnects are present or not? Or am I reading too much into, or not properly understanding,this publication from Middle Atlantic?Not really.... My comments are in regards to using the existing 80 ft 20 amp dedicated branch circuit and branch circuit/s from a sub panel with an 80 ft feeder to feed equipment that would be connected together by ics of equipment fed from the two different fed power systems. Has nothing to do with rather the equipment is rack mounted or not.
>>>>>>>>>>>>>>
Isolated ground power strip in a non-isolated rack (cont.)
A problem will exist due to the fact that all equipment with a 3-prong (grounded) plug has the power cord ground conductor bonded toIn the above quoted info the author is talking about commercial building power wiring situations. Problems a person would not normally encounter in a single family dwelling unit, imo.
the chassis. When this rackmounted equipment is screwed to the rackrail, an inadvertent ground connection will be present, defeating
the isolation!"
You are not going to use an isolated ground system are you?
If you install a sub panel, as you said, about 10 ft from the rack I see no problem.
Branch circuit runs will be short, less than 20 ft. (Figuring up and down or around.)
80 ft? Is that straight as the crow flies? Did you figure up, down, and around?
In the sub panel you will have an isolated neutral bar and an equipment ground bar. Sizing all conductors the same will a sure both the neutral bar and the ground bar will be at the same ground potential.
So if you are worried about the possibility of the neutral conductor and equipment grounding conductor not being at the same ground potential at the sub panel make all the feeder conductors the same size....
Minimum size feeder wire I would recommend, #4 awg copper. Breaker size 60 or 70 amp.
Electrical panel, copper bus only..... No aluminum bus.