07-12-11: Jedinite24I think shielded isolation transformers can effectively attenuate (filter) voltage transients (voltage spikes) through two mechanisms, if their rating is sufficient to handle the level of spike;
Nope it doesn't and I can't I can't tell you why
07-12-11: Herman
It may attenuate a spike but won't eliminate it.
An ideal transformer will pass any changes in the primary to the secondary so any spikes, surges, sags, or distortions in the incoming signal theoretically get passed through.
1) The Faraday Shield shunts energy to ground(& common mode noise)
2) Lenz's Law (see animation at link) which loosely translates to "The Induced current is such as to OPPOSE the CHANGE in applied field."
Electricity and controls for HVAC/R By Stephen L. Herman, Bennie L. Sparkman
The reason a transformer can greatly reduce any voltage spikes before they reach the secondary is because of rise time of current through an inductor. The current in an inductor rises at an exponential rate, Figure 18-3. As the current rises in value, the expanding magnetic field cuts through the conductors of the coil and induces a voltage that is opposed to the applied voltage. The amount of induced voltage is proportional to the rate of change of current. This simply means that the faster the current attempts to increase, the greater the opposition to that increase will be. Spike voltages and currents are generally very short in duration, which means they increase in value very rapidly, Figure 18-4. This rapid change of value causes the opposition to the change to increase just as rapidly. By the time the spike has been transferred to the secondary winding of the transformer, it has been eliminated or greatly reduced, Figure 18-5.