The 15amp circuit breaker (which is the on off switch for the amp) blows after 20seconds.
Now that is a horse of a different colour!
Primary winding inrush current draw of the power transformer/charging electrolytic power supply caps is causing the circuit breaker on the amp to trip open......
The 50' cord is working like a soft start circuit limiting the inrush current draw to the Cary amp. At least that is what it sounds like to me.
What can you tell me about the 120V 20 amp dedicated branch circuit.
Distance from the electrical panel?
Wire size?
Electrical panel manufacture?
Another test....
Multimeter set to AC volts.
Insert the test probe leads into the unused receptacle of the duplex receptacle. Make note of the voltage reading. Cary plugged into the other recept.
While watching the meter flip the switch on the Cary to the on position. Note the reading/s of the meter.
Does the voltage sag several volts and remain low until the amp's breaker trips open? Voltage reading/s?
OR
Does the voltage sag and then swing higher than the original no load voltage? Voltage reading/s?
.