Hi Al,
I hoped you would see my post.
As Metro04 pointed out more than likely the electrical equipment grounding conductor for the branch circuits is the metallic conduit, boxes, and fittings. Back in the 1970s that was acceptable per NEC and more than likely NYC codes. (Problem, years later, was the degradation of electrical continuity integrity from the fittings, connectors, lock nuts, and conduit couplings.
Corrosion for one, = resistance. If we have resistance then a difference of potential can exist from the grounded neutral conductor and the safety equipment grounding conductor at the branch circuit outlet device, the receptacle.
To rule any chance of noise on the safety equipment ground I would think, for test purposes, a ground cheater could be installed on the power cord of the Cary Amp.
What are your thoughts on the magnetic field of the 3rd and 5th harmonic on the relay solenoid of a magnetic breaker? I would think it would distort the actual current passing through the switch/magnetic breaker on the back of the Cary amp.
Harmonics is about the only thing I can think of that causes the Amp's magnetic breaker to trip in the OP's apartment but no where else outside of his apartment.
The fact that the 50' extension cord stops the nuisance tripping is interesting.....
I assumed the cord is coiled up and not laying out in the room. Appearance as well as being a trip hazard.
So, to me, at least two things are at play.
Size of the conductors of the cord.... Impedance....
Cord is coiled up...... inductance.....
Does that filter out harmonics or at least lessen the effect on the magnetic field of the solenoid of the magnetic trip of the breaker?
I asked the OP in a previous post if he was shutting down the Cary Amp by first pushing the power button on the front panel of the Cary putting the Amp in standby before turning off the power switch/breaker on the back of the amp. (Not doing so leaves the amp in the "Active Mode" state.)
The owners manual recommends not shutting off the amp without first putting the amp in standby.
With the problem the OP is having, unique only with his apartment, proper shutdown and power up could just be enough for the breaker to hold.
I would recommend the OP power up the amp with the 50' extension cord power off by putting the amp in "standby" first then turn off the switch/breaker.
Remove the 50' cord and plug the amp directly into the wall receptacle. Wait at least 5 minutes to power up the amp again. (Power supply caps should be bled off by then?)
I would then turn on the switch/breaker and see what happens. Hopefully the 20 second timeline will pass with no breaker trip event.
If the breaker does not trip, fingers crossed, I would not get in any big hurry to push the power button on the front of the amp that starts the sequence to power up the amp in the "Active Mode". Wait at least a few minutes or so.
If the amp does power up I would not power the amp totally down unless going on vacation or in the event of lightning storms. I would just push the power button on the front of the Cary putting the amp in standby.
Does it totally solve the OP's no.... And sad to say he would still need to keep the 50' extension cord. If he has a power outage the amp will be set to "Active Mode" and he will have to use the 50' cord to to reset the amp to standby.
Jim
I hoped you would see my post.
As Metro04 pointed out more than likely the electrical equipment grounding conductor for the branch circuits is the metallic conduit, boxes, and fittings. Back in the 1970s that was acceptable per NEC and more than likely NYC codes. (Problem, years later, was the degradation of electrical continuity integrity from the fittings, connectors, lock nuts, and conduit couplings.
Corrosion for one, = resistance. If we have resistance then a difference of potential can exist from the grounded neutral conductor and the safety equipment grounding conductor at the branch circuit outlet device, the receptacle.
To rule any chance of noise on the safety equipment ground I would think, for test purposes, a ground cheater could be installed on the power cord of the Cary Amp.
What are your thoughts on the magnetic field of the 3rd and 5th harmonic on the relay solenoid of a magnetic breaker? I would think it would distort the actual current passing through the switch/magnetic breaker on the back of the Cary amp.
Harmonics is about the only thing I can think of that causes the Amp's magnetic breaker to trip in the OP's apartment but no where else outside of his apartment.
The fact that the 50' extension cord stops the nuisance tripping is interesting.....
I assumed the cord is coiled up and not laying out in the room. Appearance as well as being a trip hazard.
So, to me, at least two things are at play.
Size of the conductors of the cord.... Impedance....
Cord is coiled up...... inductance.....
Does that filter out harmonics or at least lessen the effect on the magnetic field of the solenoid of the magnetic trip of the breaker?
I asked the OP in a previous post if he was shutting down the Cary Amp by first pushing the power button on the front panel of the Cary putting the Amp in standby before turning off the power switch/breaker on the back of the amp. (Not doing so leaves the amp in the "Active Mode" state.)
The owners manual recommends not shutting off the amp without first putting the amp in standby.
With the problem the OP is having, unique only with his apartment, proper shutdown and power up could just be enough for the breaker to hold.
I would recommend the OP power up the amp with the 50' extension cord power off by putting the amp in "standby" first then turn off the switch/breaker.
Remove the 50' cord and plug the amp directly into the wall receptacle. Wait at least 5 minutes to power up the amp again. (Power supply caps should be bled off by then?)
I would then turn on the switch/breaker and see what happens. Hopefully the 20 second timeline will pass with no breaker trip event.
If the breaker does not trip, fingers crossed, I would not get in any big hurry to push the power button on the front of the amp that starts the sequence to power up the amp in the "Active Mode". Wait at least a few minutes or so.
If the amp does power up I would not power the amp totally down unless going on vacation or in the event of lightning storms. I would just push the power button on the front of the Cary putting the amp in standby.
Does it totally solve the OP's no.... And sad to say he would still need to keep the 50' extension cord. If he has a power outage the amp will be set to "Active Mode" and he will have to use the 50' cord to to reset the amp to standby.
Jim