Hubbell 5362. Anyone try this outlet?


It's of the Hubbell Pro class.
ptss
I use these http://www.voodoocable.net/VAPO.htm as they provide an Isolated Ground and work very well also cryo treated.

Chuck
"Voodoo" indeed. Voodoo Cable states that most audio grade receptacles do not have an isolated ground as the Voodoo Hubbell does, which is correct. What they fail to mention is, an IG receptacle in only of benefit when installed in a true isolated ground circuit (in metal conduit, with separate insulated ground conductor between the panelboard and receptacle ground pin). The receptacle box, mounting strap and conduit are insulated from the ground conductor. A receptacle with isolated ground installed in a circuit with non-metallic cable (12/2 Romex with ground) provides no benefit over a standard receptacle.
Gbart

The Hubbel web-site goes into explaining the workings of an Isolated Ground Circuit. Voodoo uses a Hubbel IG 8300 which is a standard outlet available from Hubbel just that Voodoo cryogenically treats it. And IG stands for, you guessed it, Isolated Ground.

I have not heard the one the OP makes reference to.
Yes Jea, the one on page 6.
I will check wit A Porter to see why he chose his unit.
Ptss, as a suggestion ask Albert next time he has a listing for his ports.I remember the original listing for the change over from 8300 to 5362,but can't remember the exact reason.Hope this helps.