How long are your runs? Unless they are more than 30' you are just as well running 12 gauge Romex.
If much longer, then run a 60A to a subpanel, and then run short 20A circuits to each outlet. The advantages of a 60, in addition to lower voltage drop, is that the code may let you get away with not running conduit for it. Check your local ordinances.
Never put more than a 20A breaker on a normal 15/20A outlet, regardless of wiring. It has no audible benefit, and serious safety issues.