Help with Equitech 1.5Q power conditioner


Hello all. My Equitech GFCI plug on the back keeps popping when I turn on the switches Equitech switches. Am I overloading the unit or is there an issue with the GFCI plug. It worked for a while but was always super easy to trip. I only have my Amp, preamp, TV, and speakers plugged into it. Any help would be appreciated. I am in in San Francisco bay area, are there recommendations to any place I can take to to get it looked at? With it tripping so much would replacing the gfci plug with a new one help (wonder if the current one is worn out?). It is out of warranty and I do not have the box it came in to ship. Thanks!

califortini

@jea48 my bad the link has the incorrect image. I'll add mine. The top left is the receptacle that has the reset button. The only devices are the TV, 2 speakers, preamp and amp are all that are plugged into the 1.5Q. none of which are plugged into the gfci plug - those are all plugged into the regular outlets on the back

Post removed 

Oh, now I get it.

GFCI outlets do go bad, but it could also be equipment with a leaky capacitor to ground or a reactive load, which is most likely with bigger motors and amps.

If you find the problem is only your amp, I’d suspect swapping a GFCI won’t help.

Sometimes these trips happen intermittently, so hard to diagnose fully. Of course another alternative is to see if you can trigger any other outlet.  Maybe take the suspect piece of gear to your kitchen counter and see if you can trigger one of those outlets.

Post removed 

Hi @jea48  - Not my first time going through a balanced power system, though it is the first time I've known about GFCI on an example.  I read through your explanation, which is what I remember.  The part that I don't get is how a GFCI, connected to the secondary windings, tripping on a balanced power system would not also trip the kitchen outlet.

As you point out, the ground is not part of the GFCI sensing strategy in either case, but it's the imbalance between the current carrying conductors (which ground should not be except on a fault) which causes the trip.