stickman451 said:
I will contact Furutech distributor to confirm whether not the outlets are truly ’isolated’ ground and go from there.
I assume Furutech receptacles are Listed by a recognized third party testing laboratory, such as UL.
If the duplex receptacle is an IG, Isolated Ground, per NEC it will have a triangle near the "U" shaped ground contact hole.
Here are a couple more pictures of IG duplex receptacles.
https://www.zoro.com/search?q=Isolated+Ground+Receptacles&gclid=CPmd0r_0oNACFQiUaQodSSoOxg&g...
At the time the electrician looked at the job with you, you must not have had the duplexes to show him. You must have just told him they were IG receptacles. That is the only reason the electrician should have installed 4 wire branch circuit wiring for a 120V dedicated circuit. By code he needed a second equipment ground wire for the metal box. (Unless the branch circuit raceway is hard metallic metal conduit like EMT (thin wall) for example, then the box ground can be the conduit per NEC providing it is a continuous run from the box to the electrical panel. The conduit can connect to other electrical metal boxes along its’ way to the electrical panel.)
Is the wire 6-3 with ground NM-B cable, Romex? If so, there is no reason to ever use an IG receptacle when NM-B cable is used.
Just a guess the electrician used steel boxes because of the #6 wire you wanted him to install. Just a guess he installed a deep 1900, 4" x 4" X 2 1/8" deep box, with a 1 gang raised device cover, for a single duplex receptacle. He may have needed the bigger box to meet the percentage of fill required by NEC for the #6 wire.