gdnrbob,
You won’t find any SPD that will protect your home from a direct lightning strike.
If you find a manufacture that claims it will you best read the fine print.
Like westom said in his post the earth connection is the most important part for protecting your home from a nearby lightning strike.
Again, read this PDF. Lightning is lightning and the earth is the earth whether it is at a commercial office building, industrial facility, or you home. Same principals apply.
http://www.p3-inc.com/images/grounding_for_pq_wp2016_p3.pdf
As for the Siemens SPD I do not have any opinion one way or the other.
https://www.youtube.com/watch?v=7Dj33YVppDk
If it says it will protect from a direct lightning strike thought, it will not... It may not even protect your electronics in your home from a nearby lightning strike. The only 100% sure way to protect your audio and video equipment during a lightning storm is to unplug it from the wall receptacle. Same goes for any coax cable connection from a cable TV provider or a satellite dish. Same goes for an Ethernet cable connection from a router that is connected to the outside world by cable or a phone line.
I found this Website while doing a search. The guy does a pretty good job and shows some spec comparisons of different manufactures SPDs.
https://www.stevejenkins.com/blog/2014/10/whats-the-best-whole-house-surge-protection/
Here is a great video to watch. I attended a power quality surge protection seminar a couple of years ago and seen the demonstration first hand.
https://www.youtube.com/watch?v=5Wb79cXmSlc
The thing that I visually remember most is the SPD should be installed as close as possible to the load side of the electrical service panel main breaker. The first two breaker spots on ether side of the panel is where the 2 pole breaker for the SPD Line 1 & 2 to connect. (IF there are breakers in the two spots, needed for the SPD’s
2 pole breaker, have the electrician move them elsewhere in the panel. It will take him 5 to 10 minutes tops!) Mount the SPD as close as possible to the outside of the panel enclosure where the 2 pole breaker is installed. The wire leads from the SPD should be kept short.
IF The SPD is installed inside the electrical panel, hidden from view, how will you be able to see the indicating lights on the unit telling you the device is still good and working properly? SPDs that use MOVs do not last for ever. That’s why the good SPD devices have multiple MOVs for each surge function of the device. You should always check the SPD after any lightning storm in your area.
Any sub panel after the main electrical service main panel also needs an SPD installed. Again the SPD should be installed as close as possible to the feeder conductors, wires, feeding the sub panel. The first two breaker spots for the SPD’s
2 pole breaker installation.
MAKE SURE you have the electrician check the main grounding system (Grounding Electrode System) for your home’s electrical service. Clean, if needed, and tighten all connections.
No such thing as over kill here.
And as westom said, a single point earth connection is a must. All earth connections should connect to a single point to the electrical service entrance neutral conductor.
.
You won’t find any SPD that will protect your home from a direct lightning strike.
If you find a manufacture that claims it will you best read the fine print.
Like westom said in his post the earth connection is the most important part for protecting your home from a nearby lightning strike.
Again, read this PDF. Lightning is lightning and the earth is the earth whether it is at a commercial office building, industrial facility, or you home. Same principals apply.
http://www.p3-inc.com/images/grounding_for_pq_wp2016_p3.pdf
As for the Siemens SPD I do not have any opinion one way or the other.
https://www.youtube.com/watch?v=7Dj33YVppDk
If it says it will protect from a direct lightning strike thought, it will not... It may not even protect your electronics in your home from a nearby lightning strike. The only 100% sure way to protect your audio and video equipment during a lightning storm is to unplug it from the wall receptacle. Same goes for any coax cable connection from a cable TV provider or a satellite dish. Same goes for an Ethernet cable connection from a router that is connected to the outside world by cable or a phone line.
I found this Website while doing a search. The guy does a pretty good job and shows some spec comparisons of different manufactures SPDs.
https://www.stevejenkins.com/blog/2014/10/whats-the-best-whole-house-surge-protection/
Here is a great video to watch. I attended a power quality surge protection seminar a couple of years ago and seen the demonstration first hand.
https://www.youtube.com/watch?v=5Wb79cXmSlc
The thing that I visually remember most is the SPD should be installed as close as possible to the load side of the electrical service panel main breaker. The first two breaker spots on ether side of the panel is where the 2 pole breaker for the SPD Line 1 & 2 to connect. (IF there are breakers in the two spots, needed for the SPD’s
2 pole breaker, have the electrician move them elsewhere in the panel. It will take him 5 to 10 minutes tops!) Mount the SPD as close as possible to the outside of the panel enclosure where the 2 pole breaker is installed. The wire leads from the SPD should be kept short.
IF The SPD is installed inside the electrical panel, hidden from view, how will you be able to see the indicating lights on the unit telling you the device is still good and working properly? SPDs that use MOVs do not last for ever. That’s why the good SPD devices have multiple MOVs for each surge function of the device. You should always check the SPD after any lightning storm in your area.
Any sub panel after the main electrical service main panel also needs an SPD installed. Again the SPD should be installed as close as possible to the feeder conductors, wires, feeding the sub panel. The first two breaker spots for the SPD’s
2 pole breaker installation.
MAKE SURE you have the electrician check the main grounding system (Grounding Electrode System) for your home’s electrical service. Clean, if needed, and tighten all connections.
No such thing as over kill here.
And as westom said, a single point earth connection is a must. All earth connections should connect to a single point to the electrical service entrance neutral conductor.
.