If isolation transformers did that protection, then a utility transformer that provides AC power means no anomalies exist. Other potentially destructive anomalies act just like lightning. We simply use lightning as an example of all other potentially destructive anomalies created by stray cars, grid switching, tree rodents, linemen errors, and wind.
Even existing buildings must have earth ground inspected - often upgraded. Any earth ground that only meets today's human safety codes (ie NEC) is often insufficient earthing for appliance safety. Plenty of questions about earthing should exist. Even underground service does not protect from surges - including direct lightning strikes.
For example, a separate structure may require its own 'whole house' solution. Generally a separation of more than 25 feet is a ball park number for a building that is not protected by 'whole house' protection in a main building.
Back to that isolation transformer - one that is already doing your 'primary' protection. Same earthing requirements that make your 'secondary' protection layer effective also must be inspected in that 'primary' protection layer. More reasons why so many previous paragraphs should have resulted in plenty of questions. Even a transformer in an Equi-Tech cabinet is only as effective as its earth ground.
Even existing buildings must have earth ground inspected - often upgraded. Any earth ground that only meets today's human safety codes (ie NEC) is often insufficient earthing for appliance safety. Plenty of questions about earthing should exist. Even underground service does not protect from surges - including direct lightning strikes.
For example, a separate structure may require its own 'whole house' solution. Generally a separation of more than 25 feet is a ball park number for a building that is not protected by 'whole house' protection in a main building.
Back to that isolation transformer - one that is already doing your 'primary' protection. Same earthing requirements that make your 'secondary' protection layer effective also must be inspected in that 'primary' protection layer. More reasons why so many previous paragraphs should have resulted in plenty of questions. Even a transformer in an Equi-Tech cabinet is only as effective as its earth ground.