Dedicated 20 amp lines/should i use a sub panel


Happy New Year to all!!

I am about to install 3 - 20 amp dedicated lines for my stereo. I still have space in my 200 amp main panel but was wondering if their is any benefit to installing a 60 amp sub panel for the 3 audio circuits , also as i am using 10 gauge wire and its not the easiest to manipulate should i hook up the bare wire to the receptacles looped around the screws or inserted in the holes or should i use spade connection's. any advice would be appreciated.

Thanks in advance
Chris 
spinner1
Thank you, Larry (lak). Jim (Jea48) is the expert when it comes to electrician-type matters, and hopefully he’ll chime in. But FWIW I agree with all of the comments by Dill. I doubt that adding a sub-panel would provide any benefit, and as Dill indicated inserting additional contacts into the path won’t be helpful.

Unless, that is, the sub-panel is something like those made by Equi=Tech which incorporate a high quality transformer and would provide balanced power to the system. However their models cost in the vicinity of $10K or more, and weigh upwards of 300 pounds.

Good luck. Regards,
-- Al

Post removed 
Jim, Some replies below.

By side by side, do you mean the breakers are installed directly across from one another? Connected to the same main bus breaker tie. (Both are fed from the same leg, Line.) Or, do you mean one is installed above the other, side by side? One fed from leg, Line 1 and the other fed from Leg, Line 2?
>>> Same leg/busbar. One 20A breaker above other.

Did you use Romex?
>>> Yes. 8/2 NM-B (not 10 as I said before) cable from Lowes.

Did you try to keep the 2 cables separated from one another at least 6" after getting them out of the electrical panel, as soon as practical? Especially a long parallel run?
>>>Yes. 12 feet apart.

Is it possible one of the 2 is running parallel next to some other branch circuit?
>>>It’s possible but not obvious.

>>>I also tried tying the ground wires to the same terminal, removing the ground (to test only) and moving other equipment to different runs to no avail. I’ll be honest, I abandoned messing around with it after an hour and removed one leg and used the cable for another project. The one 8/2 run on a 20A breaker into a 20A L5-20/L5-20P receptacle/plug sounds great.
Post removed 
Besides having built-in noise cancelling features, and surge protection, another advantage to the sub-panel is that you end up with a star grounding scheme that is short, and therefore much less likely to cause differences in ground potential.

The biggest source of noise in my mind is usually other household appliances, and dimmer switches. If you get separate runs, without any noise cancelling, you are literally just making it easier to pick up noise from anywhere in the house. Having a 30 to 60 Amp subpannel that has its own noise and surge protection is the key.