gdnrbob2,190 posts01-07-2019 1:21pm
@jea48 ,
Would you recommend getting a DC blocker for every system?
I know not all lines have DC, but just as a precaution?
Bob
No, I wouldn’t. There is not any need for a blocker unless you have DC offset on the AC mains. If you have a piece of equipment with a torid transformer that is buzzing loudly then it may be being caused by DC on the mains. The best way to find out is to measure for it. Measure for it the correct way.
I am surprised there is not someone building a low-pass filter device to use on the AC mains to measure for DC on the mains using a regular DMM.
For a DIY project it would be pretty simple to make one.
All you need is,
1 - male plug (to plug into the wall outlet)
1 - 100K 1 watt resistor
1 - 22uF non-polar capacitor
2 - alligator clips for the probes of the DMM
Maybe a short piece of 2 wire zip cord
Soldering Iron
Solder
You could even install the resistor and cap in a small PVC plastic box with cover. Connect a short 2 wire power cord and male plug. Install a couple of recessed insulated female jacks for inserting of the probes of a DMM.
Jim
.