danvignau
First, it isn’t clear what’s meant by a "30 amp circuit." If we’re talking about the U.S., many local electrical codes - including that in my town - would require a 30A receptacle for that circuit. That would then necessitate putting new connectors on the ends of any equipment that would be plugged into that circuit, because a 30A receptacle isn’t compatible with a 15A or 20A plug. That’s a lot of work for something of little potential benefit.
A better solution would be to use 10 gauge wiring, but use a 20A breaker and 20A receptacle, resulting in a "de-rated" circuit. That would comply with both NEC and local code. I’ve done this with my system with great success. ( Some receptacles will not accept 10 gauge wire, but you can use a pigtail if that’s the case.)
However, using such dedicated, de-rated lines is no assurance that the power will be any cleaner than it is at the service panel itself. Under those conditions, there’s no question that a power conditioner can be of great benefit and - for the naysayers in our midst - it’s the sort of thing that can be shown with measurements.
A dedicated 30 amp circuit (10 guage wiring) costs less than expensive cords and works better than running these wires from a 15 or 20 amp circuit. With this 30 amp circuit, power conditioners are moot.It isn’t exactly clear what’s being recommended here, but I disagree with it in any event.
First, it isn’t clear what’s meant by a "30 amp circuit." If we’re talking about the U.S., many local electrical codes - including that in my town - would require a 30A receptacle for that circuit. That would then necessitate putting new connectors on the ends of any equipment that would be plugged into that circuit, because a 30A receptacle isn’t compatible with a 15A or 20A plug. That’s a lot of work for something of little potential benefit.
A better solution would be to use 10 gauge wiring, but use a 20A breaker and 20A receptacle, resulting in a "de-rated" circuit. That would comply with both NEC and local code. I’ve done this with my system with great success. ( Some receptacles will not accept 10 gauge wire, but you can use a pigtail if that’s the case.)
However, using such dedicated, de-rated lines is no assurance that the power will be any cleaner than it is at the service panel itself. Under those conditions, there’s no question that a power conditioner can be of great benefit and - for the naysayers in our midst - it’s the sort of thing that can be shown with measurements.