magneplanman OP4 posts
12-10-2019
11:44am
One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start. It ended up going away. Only thing I can think of that made the problem go away, was I went from having the thermostat set at 76 to 72, which definitely reduced the indoor humidity.
Repeat:
One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start.@ magneplanman
I assume you are referring to the 15 amp "Master Power" On-Off/circuit breaker on the rear panel of the amp. Is that correct? The "Master Power" circuit breaker was tripping immediately when powering from a cold start?
See page 6 of manual.
E. MASTER POWER:The Master Power switch is used to apply or remove power to the amplifier. By contrast, the Power switch on the front panel is used to switch the amplifier between standby mode and full power on.See page 10.
MAIN CIRCUIT BREAKER: The Master Power switch on the rear panel doubles as a circuit breaker. If the circuit breaker trips into the off position, try flipping it back on. If it immediately trips back off, unplug the amplifier from the power source and have it serviced.https://downloads.monoprice.com/files/manuals/14566_Manual_160414.pdf
One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start. It ended up going away.
"It ended up going away. "
As in the breaker no longer works?
Please respond if the above circuit breaker was the device tripping immediately on a cold start up of the amp.I also would like you to move the "Main Circuit Breaker" (rear panel on the amp) to the off (O) position. Verify in the off position the unit is dead, no power, lights, ect...
As for the dedicated branch circuit GFCI breaker that feeds the amp. Going from what you posted it was/is high inrush current draw from the amp that was causing the 15 amp breaker at the amp to trip open. Assumption, the breaker no longer works. The GFCI breaker was next in line to protect the branch circuit wiring. (You never mentioned what manufacturer the electrical panel/breaker is. It would be nice to know) Note. It would be safe to say it is the Thermal-magnetic section of the AFCI breaker that is causing the breaker to trip open. The high inrush current draw of the amp is causing the breaker to trip open.
Is the AFCI breaker weaker now after several tripping events than when it was when it first tripped opened? Probably. Will installing a new breaker solve your tripping problem? For a while. Band-aid repair.
.