@Hilde45, when you measured the 4 volt difference between safety ground and the miswired "hot" terminal on the outlets was some or all of the equipment plugged in at the time? If so, I think it would be worthwhile to repeat that measurement with the equipment unplugged. In addition to the possible causes Erik has cited for the 4 volt measurement I’m thinking that applying 120 volts to the neutral of whatever equipment was plugged in could have resulted in AC leakage to ground within the component(s) that might have been responsible.
Jim ( @jea48 ), does that sound plausible to you?
I’m thinking that applying 120 volts to the neutral of whatever equipment was plugged in could have resulted in AC leakage to ground within the component(s) that might have been responsible.
Jim ( @jea48 ), does that sound plausible to you?
Al, (almarg), yes I would think that is a possibility too. Any connected load along the entire length of the branch circuit.
Also as I said previously.
1) VD, (Voltage Drop), on the neutral conductor due to the connected load on the branch circuit.
2) An induced voltage that is/may be created by the hot and neutral current carrying conductors onto the equipment grounding conductor.
4Vac would be pretty high in my opinion though.
Here is another possible reason:
IF there was a decent size load connected to the circuit at the time the 4 volts was measured it could be caused by a slightly loose and or corroded neutral connection anywhere from the panel neutral bus connection to the outlet the OP measured the 4 volts.
It would be interesting to know if the other branch circuit the OP measured 124Vac on is fed from the same Line,Leg, as the circuit he is experiencing the problem on. If yes, the 4V could very well be caused by a slightly loose and or corroded neutral wire connection in the branch circuit. That is one of the problems with using the duplex outlets for making the in and out connections for the branch circuit wiring. Though I have seen the same thing happen with a slightly loose and or corroded joint where a cheap hard plastic wirenut was used.
Though none of the above has anything to do with the AC reversed polarity problem the OP is experiencing.
Jim.