Correction:
jea483,299 posts"4Vac would be pretty high in my opinion though."
03-22-2020
2:57pm
Also as I said previously.1) VD, (Voltage Drop), on the neutral conductor due to the connected load on the branch circuit.4Vac would be pretty high in my opinion though.
2) An induced voltage that is/may be created by the hot and neutral current carrying conductors onto the equipment grounding conductor.
That statement was meant for #2 only.
( An induced voltage that is/may be created by the hot and neutral current carrying conductors onto the equipment grounding conductor. )
It does not apply to #1.
hilde45 OP286 postsIf you would have said the branch circuit wiring you were having the problem with is DIY, I would tell you to hire an electrician to find and fix the problem/s.
03-22-2020
2:35pm
So, our house is a mixture of old/DIY and new (renovation); the problem is with the old part of the house.
Is the wiring in the old part of the house original wiring? Any idea what year that part of the house was built?
Just a guess the branch circuit wiring you have been troubleshooting is 14 gauge. The breaker in the panel is a 15 amp.
Just a guess there is maybe 6 to 8 duplex receptacles on the circuit. At present you have not posted if there are any ceiling light fixtures on the circuit.
By chance do you know what type of wiring the branch is? Is any of it exposed where you can see it? Maybe a back side of an unfinished wall? Maybe in the room the electrical panel is located?
Examples of the type of the branch circuit wiring:
Romex?
Thin wall rigid (EMT) Conduit and wire?
BX? (Wire with an outer flexible interlocked steel armor).