Guys, way to much time has been spent on this thread about the OP measuring a difference of potential, voltage, of 4 volts, from the neutral to the equipment ground contact on the receptacle outlet.
His biggest problem is reversed AC polarity he measured at the outlet. And as he has later posted the same reversed polarity he measured at other outlets on the same branch circuit.
As for the 4 volt the OP measured was it really 4Vac? Who knows.
I just checked a duplex receptacle that is fed by a 20 amp dedicated branch that is used to feed a treadmill. The branch circuit is #12/2 with ground Romex that is about 40ft from the electrical panel at best.
The test:
Multimeter, a Fluke 87. First test, meter set to AC volts. Default range auto scale. Reading,
power switch turned on treadmill only, standby state. Belt not running. Line voltage, 121.5Vac. Neutral to equipment ground, 9.4mv. (Meter allowed to settle down). Note, mv....
(Note Motor in treadmill is DC. That means the power supply is DC. Noise?)
I changed the range setting on the multimeter to 400Vac That is the closest range available above 122Vac.
Line voltage, 121.8Vac. Neutral to equipment ground contact, (after the meter settled down after about 10 sec or so), a steady 0.3Vac.
The above is for one finite test only. A different connected load, and type of load, no doubt would yield different results. No doubt a different, longer branch circuit with different connected loads would make a difference. I could go on and with different scenarios that would, could, make a difference in the neutral to equipment ground difference of potential, voltage.
What really matters? The conductivity, integrity (for a lack of a better word), of the equipment ground to be able to safely carry a ground fault current back to the source and hopefully cause the branch circuit breaker to trip open. (Note. In the event of a bolted ground fault event the instantaneous current could very well exceed 1000 amps.)
Jim
.
His biggest problem is reversed AC polarity he measured at the outlet. And as he has later posted the same reversed polarity he measured at other outlets on the same branch circuit.
As for the 4 volt the OP measured was it really 4Vac? Who knows.
I just checked a duplex receptacle that is fed by a 20 amp dedicated branch that is used to feed a treadmill. The branch circuit is #12/2 with ground Romex that is about 40ft from the electrical panel at best.
The test:
Multimeter, a Fluke 87. First test, meter set to AC volts. Default range auto scale. Reading,
power switch turned on treadmill only, standby state. Belt not running. Line voltage, 121.5Vac. Neutral to equipment ground, 9.4mv. (Meter allowed to settle down). Note, mv....
(Note Motor in treadmill is DC. That means the power supply is DC. Noise?)
I changed the range setting on the multimeter to 400Vac That is the closest range available above 122Vac.
Line voltage, 121.8Vac. Neutral to equipment ground contact, (after the meter settled down after about 10 sec or so), a steady 0.3Vac.
The above is for one finite test only. A different connected load, and type of load, no doubt would yield different results. No doubt a different, longer branch circuit with different connected loads would make a difference. I could go on and with different scenarios that would, could, make a difference in the neutral to equipment ground difference of potential, voltage.
What really matters? The conductivity, integrity (for a lack of a better word), of the equipment ground to be able to safely carry a ground fault current back to the source and hopefully cause the branch circuit breaker to trip open. (Note. In the event of a bolted ground fault event the instantaneous current could very well exceed 1000 amps.)
Jim
.