I touched the red probe to the center and the black probe to the sides of the can and got 117 volts. That seems like the polarity is correct.Assuming that the "can" you refer to is the socket into which a light bulb is inserted you were measuring between hot and neutral, rather than between safety ground and each of the other two wires (hot and neutral) as you were doing on the outlets. And if so, the measurement says nothing about polarity. Since this is AC you would have obtained the same reading if you reversed the connections of the red and black probes.
I’m surprised, though, that the reading was only 117 volts, and I'm not sure what to make of that. At the miswired outlets you variously measured 3.4 to 4 volts between ground and the miswired neutral, and 120 volts between ground and the miswired hot. And you measured 124 volts between ground and hot on other outlets in the same basement that are properly wired. As Jim pointed out earlier 120 + 4 = 124 volts, which seems unlikely to be a coincidence.
On the miswired outlets what do you measure between hot and neutral? As far as I can recall that has not yet been measured.
Best,
-- Al