For a sub panel in an out building, separate building, a ground rod (Grounding Electrode) is required. The ground rod is connected to the equipment ground bar in the sub panel creating a grounding electrode system for the separate building.
For a sub panel located in the same building as the main electrical service panel the separate earth connection ground is not required. If not required why would anyone want it? The separate earth connection can/does cause more harm than good. In fact the separate earth connection can/will add noise to the branch circuit equipment grounding conductors connected to the earth connected ground rod.
This guy has helped over the years in writing parts of the National Electrical Code, (NEC).
Auxiliary Grounding Electrode. (NEC 250.54)
https://www.youtube.com/watch?v=gg4wBI7bWgI
.
For a sub panel located in the same building as the main electrical service panel the separate earth connection ground is not required. If not required why would anyone want it? The separate earth connection can/does cause more harm than good. In fact the separate earth connection can/will add noise to the branch circuit equipment grounding conductors connected to the earth connected ground rod.
This guy has helped over the years in writing parts of the National Electrical Code, (NEC).
Auxiliary Grounding Electrode. (NEC 250.54)