You’ve gotten great advise so far. To summarize / reiterate,
1) If possible don’t limit yourself to one dedicated line, it limits your flexibility for gear placement. I have two dedicated lines installed on both sides of my room (30’W x 15’D), no ground loop hum :-)
2) Another vote for Environmental Potentials EP-2050, add EP-2750 Ground Filter to the main panel as well.
3) Use atleast 10awg wire for 20amp dedicated circuit.
Once you have installed dedicated lines, it does not matter how you group your components on each line. As far plugging your gear, I will PM you couple of options to consider.
Good luck!