Guys don’t forget to figure branch circuit wiring VD (Voltage Drop).
Example:
For a 60ft branch circuit using #14awg cu wire during short peaks of 12 amps current draw.
FWIW a 15 amp breaker will pass short quick draws of current well over the 15 amp handle rating all day long with out tripping. VD will be proportional to the length of the branch circuit wiring and the higher current draw on the circuit.
.
Example:
For a 60ft branch circuit using #14awg cu wire during short peaks of 12 amps current draw.
Voltage drop: 3.8515 amps.
Voltage drop percentage: 3.21%
Voltage at the end: 116.15
Voltage drop: 4.81https://www.calculator.net/voltage-drop-calculator.html?necmaterial=copper&necwiresize=0&nec...
Voltage drop percentage: 4.01%
Voltage at the end: 115.19
FWIW a 15 amp breaker will pass short quick draws of current well over the 15 amp handle rating all day long with out tripping. VD will be proportional to the length of the branch circuit wiring and the higher current draw on the circuit.
.