I'm not advocating adding ground rods but here is my experience as an Eng Mgr over Test Equipment in an Aerospace Mfg plant. We made product that operates in the 0-10 mA range. So the test equipment must be very quiet in order to generate clean plots. We started having some noise issues of say 0.5-1 mA which is enough to make the plots look bad on one of the test stands. My test engineer suggested sinking a ground rod through the floor right next to the test stand so that the chassis could be grounded. Our facilities mgr was not on board with that plan until we showed him that the building ground was floating at 500+ mA! The ground rod worked. To be effective the ground wire must be thick and short. The ground rod must be near the equipment. The ground was connected to the chassis only.
Adding ground rods just because may not be wise. Proper measurement and analysis of the electrical noise should be done first and then determine the best course of action. BTW- our products fly on airplanes. Therefore, they are operating in the 0-10 mA range with no earth ground.