Fremer's Single-leg panel is absolute tweak bs


So a few months ago a video appears on Youtube with Michael Fremer and some electrical contractors installing a custom electrical service and extravagant ground rod array.

OK, but the one thing about it that’s absolute unnecessary tweaky BS is the idea of running a single leg to a sub panel, as well as only using one leg for the audio equipment in it. Who ever thought this was a good idea? It isn’t.

If you really want to get as high-end tweaky as you can this is the absolute wrong way. Run 6 gauge or larger to a sub pane.  In that sub panel you locate a 220V to 120V step down transformer and keep everything balanced all the way to the outlets. That is the best of all worlds.  High noise rejection, meets code, balanced current draw from both legs and extremely low voltage drop from the utility pole to the outlets.

Another good alternative is to run 220V to a wall outlet, and use a high quality step down transformer there. A 220V/30A circuit becomes 60A at 120V output. Running high voltage as close to the outlets as possible doubles your wire gauge effectiveness.

 

 

erik_squires

Lets keep this narrowly focused on discussions of 1 leg or 2 to a panel, and best practices. 

I've always liked the logic of using two legs to share (and halve) the current load, as it pertains to larger motors in a residential circuit.  Each leg is much farther below it's theoretical current limit.  Not sure if or how any of that translates to sound quality, but the reduced current flow per leg still makes sense to me regardless of the application. 

Jea, I have measured with a meter a reduction in noise in a panel when its grounded properly. I have eliminated certain noise. Yes you can shunt noise when you ground properly. Grounding is far more technical than a rod in the earth.

But look.  I'm a business.  Its my sole income now.  I laid off all my employee and stopped doing restaurants and houses.  For more reasons than just being a crazy audiophile.  If you want to really understand grounding you need to do the work . Take the Lyncole classes.  Read the Sores books.  Read the Morrison books.  Watch the Holt Video.  Talk to other people who do as I do.  There are a couple others out there.  For the most part they do recording studios.  There are business dedicated to grounding and they get big money to tell data center and hospitals, labs, military etc how to ground properly.  Finally, go out and apply what you learn.  Measure it.  You can get rid of noise if you do it right.  This idea you can't is people not doing it right. 

If you really want to scratch your head, prove to an engineer a ground box like Entreq or Altaira reduce noise.

I I'm not an electrical engineer or electrician just a audio guy trying to get better sound. This is my take!

Save money by dumping the step down transformer as it adds more noise. In the USA residential single phase split 120/240 Volts, 240 Volts is more efficient then 120 Volts. 240 Volts is half the amps as 120 Volts. 240 Volts is balanced power right from the pole transformer to your house. In my opinion your audio gear will sounded better on 240 Volts then 120 Volts. 😎

Mike

@kingrex said:

I have measured with a meter a reduction in noise in a panel when its grounded properly. I have eliminated certain noise.

I have no doubt in what you say. But show me the circuit. Here is the circuit as I see it.

The EGC, IF used, >>> to the service equipment grounded conductor >>> to the neutral of the split phase secondary winding of the power transformer. There, some, of the noise energy is dissipated in the winding in the form of heat.

Mother Earth is not involved.... Show me the circuit if you think it is. Please provide any credible proof from someone like Henry Ott, as an example, who says noise can be "shunted", diverted, to mother earth. Show me the circuit if you think it is. You said, Quote: "Read the Sores books. Read the Morrison books." .... How about a quote, a White Paper, of Morrison’s that will backup your thinking.

Those in authority need to stop telling audiophiles noise on a circuit ground can be shunted, diverted, to earth. I still read current posts where audiophiles are driving a rod outside their audio room using it to replace the branch circuit EGC. Dangerous as Hell... And in the case of a bolted ground fault it will never trip the circuit breaker in the panel. Never...Works great for hunting fish worms though.

Finally this:

If you really want to scratch your head, prove to an engineer a ground box like Entreq or Altaira reduce noise.

I know nothing about the Entreq...

What I know about the Shunyata ALTRAIRA Ground System I learned from watching the video I posted above. What Gabriel has built, and his explanation of how it works, makes sense to me. He uses individual filters that are connected, to each ground post on the back of the box that are then connected to a common ground conductor. So all the filtered grounding posts are connected together.

He has two boxes. One for the Chassis ground and one the signal circuit ground. NOTE no where in the video does he promote floating, disconnecting, the EGC from any audio equipment that uses it. If fact, as I remember from watching the video, He says, and rightly so, the electrical service connection to mother earth is for lightning protection. Not for, shunting, diverting, noise to earth...

He didn’t fully explain, unless I missed it, how he treats the chassis of Class II double insulated audio equipment where an EGC is not used. That equipment is different... That equipment the Signal ground and DC B -, is connected directly to the chassis. One mistake I caught was him saying tube equipment designers connect the signal ground and DC B - directly to the chassis. That’s not true. Some might, but not all.

What I did find interesting, if true, some equipment noise the rectifier(s) make in the DC power supply(s) circuit designers dump it onto the chassis. Maybe Gabriel could show them how to install a filter between the signal ground, DC B - , and chassis. That would solve a lot problems.

.

Jim

.

I really don’t understand where Erik gets the idea the grounding I did was extravagant. Its code??????? Go read NEC Article 250.

Extravagant is the difference between what the NEC would require (minimum 2) and what was installed.

As in many cases, the NEC often specifies the minimum requirements, not the maximum. You can be NEC code compliant and extravagant at the same time. But really, that entire post above should be memorialized.