I understand what you’re saying Erik. You’ve given me another idea. As of right now (and as with almost any), my outdoor A/C condenser’s earth ground goes back into the house, and attaches to the panelboard’s grounding bus bar. If we’re looking at lightning protection for a condenser (if it sustains a direct hit), one would want that strike to immediately discharge into the ground, *before* hitting the circuit breaker box, and *then* discharging into the ground via the ground rod(s) feeding the circuit breaker box's grounding bus bar. For many this may not be feasible, but in my case, my ground rod is right beside my A/C condenser. While maintaining the current condenser earth ground connection, I may install another low impedance earth ground directly from the A/C condenser to the ground rod (again, OCD).
Having been a Radio Broadcast Engineer for decades, this is basically the same thing we do when grounding broadcast towers. The main ground system exists around the broadcast tower (many times incorporating a ring of ten 8’-10’ grounding rods cadwelded together), so that the strike can *immediately* discharge into the ground, *before* entering a transmitter building or studio/office building. The rest of the star ground system for the facility then feeds off of this broadcast tower base ground system.