@devinplombier said:
o, essentially the outlets on the back of the Equitech are wired the same way as old 240V appliances,
No not all all.
Click on the Link below. Look at the secondary winding on the right hand side of the transformer.
https://www.electronics-tutorials.ws/wp-content/uploads/2018/05/transformer-trans63.gif
At the top of the drawing there is a lead that has IA + ___>______60V___
The bottom of the drawing there is a lead that has IB - ___>______60V___
(*Note: I added 60V to each lead.)
The 2 Hot leads, (60V + 60V = 120V between them), connect to the Hot and neutral terminals on a 120V GFCI duplex receptacle LINE. . (A GFCI duplex receptacle has LINE and LOAD connections).
It doesn’t matter which lead you connect on the neutral and Hot terminals on the GFCI duplex receptacle. (* Though ALL DUPLEX RECEPTACLES INSTALLED ON THE LOAD SIDE OF THE GFCI OUTLET SHOULD FOLLOW THROUGH THE SAME AS YOU WIRED THE GFCI OUTLET. That’s why two different colors of conductors should be used. Any two different colors other than WHITE or GRAY.
/ / /
Safety Equipment Ground that is created, wired, on the secondary side of the transformer.
Per NEC code the secondary winding of an isolation transformer shall be earth grounded. NEC code says the ground shall connect to the main grounding system (Grounding Electrode System) of the main electrical service entrance neutral conductor. (NEC allows the connection to be made at any point on the system ground.)
(Here Equitech may have violated the NEC. It depends on when the unit was made. For many years the NEC allowed the EGC at the wall outlet to be used for a grounding electrode conductor, ground. That was changed many years ago. The Equitech 1.5Q power conditioner uses the in-wall branch circuit wiring EGC, (Equipment Grounding Conductor), for the earth ground for the secondary of the transformer. The EGC ground pin on the IEC inlet connector connects, bonds, to the Equitech 1.5Q metal enclosure.
I’m getting there...
Back to the drawing of the transformer’s secondary winding.
https://www.electronics-tutorials.ws/wp-content/uploads/2018/05/transformer-trans63.gif
See the Blue line that connects to the center of the secondary winding? It has a - on top of it and a + on the bottom. This lead is the neutral Center Tap of two 60V windings.
For electrical safety the Secondary winding of an isolation transformer must be wired as a Grounded AC Power System. That is accomplished by connecting the winding center tapped neutral lead to earth ground and bonding the neutral to the metal enclosure housing the transformer. (The neutral lead from the center tap of secondary winding connects to the same point the EGC ground wire from the IEC inlet connector is bonded to the transformer metal enclosure. This is the same point that all EGCs for outlets will connect.
There is the safety equipment ground for all the power oulets.
How does it handle floating-ground loads?
There is not any floating ground loads.
One down side of a plug and play isolation transformer power system? IF the wall outlet, the unit plugs into, is not grounded...
.