Nuisance tripping of AFCI circuit breaker by inrush of current when turning on amplifiers


I recently added an Accuphase power supply for my Accuphase mono blocks.  When I turn on the second mono block it trips the AFCI circuit breaker.  I had no trouble using the mono blocks with a Puritan Audio PSM 156 power conditioner, but it is passive.  The Accuphase PS-1250 is power regenerator with a huge toroidal transformer and a large mechanical on/off switch.  I imagine either the inrush of current from the PS-1250 + 2 mono blocks is too much for the AFCI breaker or their mechanical switches are creating arcs their algorithms do not recognize as normal.

I have a 10 year old Siemens 15 amp AFCI breaker, and my question is what best to replace it with?  I have read that AFCI breakers have improved considerably with less nuisance tripping, and the first step would be to use a current model as a replacement.  But is there a better solution?

Square D makes 'High Magnetic' AFCI breakers that are less prone to nuisance tripping, but I don't know if they would even fit in my panel.  I'm not sure if Siemens makes a similar product.

An electrician coming over at the end of the week, but I thought I would ask here as this must be an issue many audio hobbyists have encountered with AFCI breakers.

toronto416

If it really is an AFCI tripping, consider swapping out power cords as well as changing the order of amplifier starts.

I do repeat though, first generation AFCI breakers (1999 ish) were more jittery than the second generation CAFCI breakers. 

Some good suggestions - thank you!

I did try changing the sequence of turning on the amps - and bingo - regardless of which one I turn on first, all is well until I turn on the second amp - this trips the breaker.  So it appears to be a load issue and not the amp switches.  Hopefully a new breaker will do the trick - 20 amp vs. 15 amp.

Trying a different circuit would entail moving the power supply (93 lbs) and the mono blocks (101.5 lbs each) to another room - 300 lbs of gear!  

 Hopefully a new breaker will do the trick - 20 amp vs. 15 amp.

I may have missed it if you mentioned it because my eyesight is bad and getting worse every day, but I assume that the circuit is wired with at least 12 gauge if not larger?  If not, you would not want to use a 20A breaker.  I was only checking because I was thinking that this may have been the reason you currently have a 15A breaker in there now.

Square D makes 'High Magnetic' AFCI breakers that are less prone to nuisance tripping, but I don't know if they would even fit in my panel.  I'm not sure if Siemens makes a similar product.

As far as this goes, I am not an electrician, but it has always been my understanding that using a breaker that is not the same brand as your panel can cause a homeowner's insurance company not to pay out in event of a fire.

 

The only circumstance under which you should change the breaker amp rating to 20 A is if you have 12 gauge wiring already.

Do not increase the amp size unless you are sure or rewire.