Nuisance tripping of AFCI circuit breaker by inrush of current when turning on amplifiers


I recently added an Accuphase power supply for my Accuphase mono blocks.  When I turn on the second mono block it trips the AFCI circuit breaker.  I had no trouble using the mono blocks with a Puritan Audio PSM 156 power conditioner, but it is passive.  The Accuphase PS-1250 is power regenerator with a huge toroidal transformer and a large mechanical on/off switch.  I imagine either the inrush of current from the PS-1250 + 2 mono blocks is too much for the AFCI breaker or their mechanical switches are creating arcs their algorithms do not recognize as normal.

I have a 10 year old Siemens 15 amp AFCI breaker, and my question is what best to replace it with?  I have read that AFCI breakers have improved considerably with less nuisance tripping, and the first step would be to use a current model as a replacement.  But is there a better solution?

Square D makes 'High Magnetic' AFCI breakers that are less prone to nuisance tripping, but I don't know if they would even fit in my panel.  I'm not sure if Siemens makes a similar product.

An electrician coming over at the end of the week, but I thought I would ask here as this must be an issue many audio hobbyists have encountered with AFCI breakers.

toronto416

The only circumstance under which you should change the breaker amp rating to 20 A is if you have 12 gauge wiring already.

Do not increase the amp size unless you are sure or rewire.

Since you said you were having an electrician come to look things over, you could ask him what he'd charge to put a separate  circuit (or circuits) using 12 or 10 gauge wire in where you want your system to live (assuming you don't want to do it yourself).  .   

Thank you Matthew - that is a good suggestion.  It is not something I would be able to do myself.

It's not that bad a job, but for me it was time consuming both times I did it, and the second time I dropped some new circuits down to a new location (a couple of years ago) I had learned a lot more than the first time I did it about 30 years ago, so I went back to those original circuits I dropped in to tidy some stuff up, and some of the stuff I had done looked almost scary to me the second time around.  So anyway, I don't think it would be cheap to get an electrician to drop a new circuit in, but the benefit your system might derive from it's own dedicated circuit(s) might be worth it to you.

Anyway, what I meant to say but I forgot, was that I am pretty sure that putting a 20A breaker on a circuit made of wire smaller than 12 gauge would be another  reason that a homeowners company could use to void your policy in the event of a catastrophe.