@richardbrand Said:
@jea48
Did you do your practical hospital wiring based on the "false" teachings from your apprenticeship, or based on what you learned here? Be honest.
I did electrical wiring after 2010 the same way as I did before 2010. Why would you think I would do it any different?
Knowing how energy actually flows from the source >>> to the Load doesn’t change anything as for installing electrical wiring.
To keep it as simple as I can for you... Example: A customer has a new piece of equipment he wants connected to electrical power. He may have a spec sheet that specifies what the manufacturer requires for the minimum electrical wiring requirements. Usually it just says it must be wired to meet NEC code. (Not Always)
If nothing is given the name/data plate on the equipment is used. The data plate will show the Phase, voltage, and the FLA (Full Load Amps).
Per NEC, (National Electrical Code), the branch circuit wiring is sized using the FLA times 125%. If the FLA is 27A, 1.25 X 27A = 33.75A. Table 310-16, (and notes), wire size? #8awg copper. That’s It.... Phase, Voltage, and Full load current. (Note: Motor loads use different wire sizing calculations)
Nothing said about current "flowing" back an forth in a circuit. Nothing said about energy flowing in one direction either... Phase, Voltage, and Full load current... (Note, there are, will be, maybe, other things the electrician must take into account, for the wiring method he uses. I kept it simple, for you.
As for this"
@jea48
You seem to accept that
Light is the fastest-moving stuff in our universe. It travels at 186,000 miles per second (300,000 km/sec)
I’d add "in a vacuum" just for completeness.
LOL, that was a quote... I really don’t think the author needed to say, in a vacuum... Most people know outer space is a vacuum.
.