The Furman specs for the 2400 are:
10 ft. captive 3/12 AWG, black cord with NEMA 20 plug. Mine is still gathered, as I only needed 3 feet, but would think 10’ is accurate.
10 ft. captive 12/3 AWG,
@signaforce define gathered. I would not coil the the remaining 7ft in a neat tight small diameter coil. Imo, a small coil would act as an inductor.
FYI do not cut off the cord to make it shorter. That more than likely would void the Furman 2400 warranty.
Just a guess, I could be wrong, the length of 10ft cord may be for the proper operation of the type 3 point of use SPD, (Surge protection Device) inside the unit. With a type 3 SPD the minimum length of the branch circuit wiring from the electrical panel to the SPD matters. The minimum length is 30ft.
Type 3– Point of utilization SPDs, installed at a minimum conductor length of 10 meters (30 feet) from the electrical service panel to the point of utilization, for example cord connected, direct plug-in, receptacle type SPDs installed at the utilization equipment being protected. The distance (10 meters) is exclusive of the conductors provided with or used to attach SPDs.
.