Correction:
The minimum AIR interrupting rating for a residential dwelling circuit breaker is 10KA. You will see it on the front of the breaker.
My bad.
That should read:
The minimum AIC interrupting rating for a residential dwelling circuit breaker is 10KA. You will see it on the front of the breaker.
AIC, (Ampere Interrupting Capacity) rating.
What the AIC of a 10KA circuit breaker means? The breaker contacts will open up to 10KA, 10,000 amps. (Don’t bet your life on it though.)
/ / / /
.
@erik_squires Said:
It may help you to understand that the MOV’s in an SPD’s for the most part deliberately CAUSE shorts (series mode an exception) which is why they must be a certain distance from the panel. This ensures the AIC of the breakers isn’t exceeded when they do short.
AIC corrected..
I know how MOVs work.
.
which is why they must be a certain distance from the panel. This ensures the AIC of the breakers isn’t exceeded when they do short.
BS. I told you the reason in my previous post.
Think about... A Bolted Line to Line, or Line to EGC fault 1ft from a circuit breaker will trip open the breaker on short circuit protection. Sure in the heck don’t need 30ft. (Where’s your protection of the breaker) Think about it... Bolted... A heck of a lot more flow of amps than any MOV could possibly return to the source.
.
The Furman with SMP won’t cause a short under most surge conditions so no AIC needed. Zerosurge/Brickwall do the same.
AIC corrected.
I never said a Type 3 SPD had a AIC, Ampere Interrupting Capacity rating.
jea48 said:
The 30ft minimum distance requirement has to do with the fault current rating of the Type 3 SPD . Any idea what the Furman is rated at?
fault current rating, is not the same as, AIC, Ampere Interrupting Capacity rating.
.
but the internet is littered with images of where these failed or caused a fire as they melted the plastic enclosures.
I seen the video. A $10.00 Type 3 SPD plug strip was used for the demonstration.
.
2020 NEC 242.16 Type 3 SPDs
Type 3 SPDs shall be permitted to be installed on the load side of branch circuit overcurrent protection up to the equipment served. If included in the manufacturer’s instructions, the Type 3 SPD connection shall be a minimum 10 m (30 ft) of conductor distance from the service or separately derived system disconnect.
No mention of MOVs;
No Exception, for Furman, Zerosurge, or Brickwall.
.