@ecat026 said:
The replacement GFCI breaker is a good alternative, if somebody manufacturers a retrofit for what is likely a 60 year old breaker box.
The OP said the house is 63 years old. (Built in 1962). If the electrical panel is the original one, IMO, the OP should be worried more about the old panel than the non grounded outlet his audio system is plugged into, when it comes to his safety. You are correct about the GFCI breaker though. I didn’t consider the panel could still be the original one that was installed in 1962. That doesn’t say the panel was made in 1962. I could be from the late 1950s. Who knows?
As for this:
**406.4(D)(2) Non‑Grounding‑Type Receptacles.**
Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (b), or (c):
I looked at that this morning and thought to myself wheres the (a) ? So I pulled out my 2020 NEC code book and read 406.4 (D) (2) (a) . I seen the little triangle beside (a)... (a) was deleted in the 2020 NEC. 2017 NEC was the last code Edition allowed. The OP lives in Maryland. To date the State of Maryland.is still working under the 2020 NEC code.
.