First, there is no such thing as "zero volts," we just agree to call something zero (the earth) and measure everything relative to it. It is completely arbitrary.
Second, neutral and ground are bonded in the sevice panel and only there. Go to Home Depot and look at a panel. The neutral bar and the ground are bonded. Another term for neutral is grounded conductor.
Third, in a house, circuits are taken off each "hot" conductor, and the currents in the grounded conductors (which are all tied together) cancel each other out. In other words, if, by chance, the currents on each hot leg were exactly equal, the grounded conductor could be disconected from the service neutral (and the ground) and every thing would work. All the current would flow through the hot legs.
Fourth, the reason the grounded conductor measures hot relative to ground is because the conductor has resistance, and there is current flowing through it. Since there should be no current flowing in the ground, and the two are tied only at the panel, there will be a voltage difference at the outlet (but not at the panel).
Fifth, Mr. Holt does not mention, although I am sure he knows, that all power is generated and transmitted as three phase, each 120 degrees apart in time. When each phase has equal current, they sum to zero and there is no net current to flow through the ground. Any current is due to the three phases being unequal and will be small relative to the total current draw. If any significant power is disipated in the Earth, the power company loses money.
The Earth naturally has absolutely enormous currents flowing in it, making the Earth into a giant magnet.
Polarity is a safety issue.
Second, neutral and ground are bonded in the sevice panel and only there. Go to Home Depot and look at a panel. The neutral bar and the ground are bonded. Another term for neutral is grounded conductor.
Third, in a house, circuits are taken off each "hot" conductor, and the currents in the grounded conductors (which are all tied together) cancel each other out. In other words, if, by chance, the currents on each hot leg were exactly equal, the grounded conductor could be disconected from the service neutral (and the ground) and every thing would work. All the current would flow through the hot legs.
Fourth, the reason the grounded conductor measures hot relative to ground is because the conductor has resistance, and there is current flowing through it. Since there should be no current flowing in the ground, and the two are tied only at the panel, there will be a voltage difference at the outlet (but not at the panel).
Fifth, Mr. Holt does not mention, although I am sure he knows, that all power is generated and transmitted as three phase, each 120 degrees apart in time. When each phase has equal current, they sum to zero and there is no net current to flow through the ground. Any current is due to the three phases being unequal and will be small relative to the total current draw. If any significant power is disipated in the Earth, the power company loses money.
The Earth naturally has absolutely enormous currents flowing in it, making the Earth into a giant magnet.
Polarity is a safety issue.