Rex, I concede to your challenge. Obviously I was wrong..... After doing some research I have found the IEC connectors are in a category all their own. The oddest thing I noticed the same connectors can be used for either 125Vac as well as 250Vac. To my knowledge I cannot think of any other plug and receptacle device that allows that here in the US.
The problem I have understanding the UL/CSA listing is where is the protection for the non savvy consumer that buys a piece of equipment that has a 20 amp IEC connector, that has a FLA rating of 16 amps, and did not come with the manufacturer supplied cord with a 20 amp plug. The guy that sold him the equipment lost the the factory cord and plug but threw in one that fit the IEC connector and had only a 15 amp plug.
The buyer knows beans about what we have been discussing here. He plugs the unit in, powers it up and everything seems to work fine. The branch he plugged into is only a 15 amp circuit and the wire is being overloaded. Hopefully the breaker will trip open. You would be surprised how many 15 amp breakers won't trip at 15 amps. Where is the protection.....
The cord and plug is not idiot proof, jmho.
Now here is an example that to me mirrors the same thing that is allowed with the IEC 20 / 5-15P power cord . As per NEC I cannot make a power cord with a NEMA 5-20R receptacle on one end and a NEMA 5-15P plug on the other end...... Can you see the difference?
The problem I have understanding the UL/CSA listing is where is the protection for the non savvy consumer that buys a piece of equipment that has a 20 amp IEC connector, that has a FLA rating of 16 amps, and did not come with the manufacturer supplied cord with a 20 amp plug. The guy that sold him the equipment lost the the factory cord and plug but threw in one that fit the IEC connector and had only a 15 amp plug.
The buyer knows beans about what we have been discussing here. He plugs the unit in, powers it up and everything seems to work fine. The branch he plugged into is only a 15 amp circuit and the wire is being overloaded. Hopefully the breaker will trip open. You would be surprised how many 15 amp breakers won't trip at 15 amps. Where is the protection.....
The cord and plug is not idiot proof, jmho.
Now here is an example that to me mirrors the same thing that is allowed with the IEC 20 / 5-15P power cord . As per NEC I cannot make a power cord with a NEMA 5-20R receptacle on one end and a NEMA 5-15P plug on the other end...... Can you see the difference?