Grounding is my biggest concern, my electrician said I can drive a 6 foot grounding rod into the ground and attach the 2 dedicated lines to it. Does this make sense?
Davea33
Find another electrician! A licensed electrician.....
As for the branch circuit wire.
If you go with #12 wire use a 20 amp breaker.
If you go with #10 wire you still must use a 20 amp breaker per code.
If you use a 20 amp receptacle by code it cannot be connected to a 15 amp branch circuit breaker. A 20 amp rated receptacle can only be connected to a 20 amp branch circuit, by code....
#12 awg copper wire is rated for 20 amps.