Bob, it's not the undersized/oversized wire issue that I was referring to. As you state, it's better to have thicker wire. It's the receptacle that I was referring to. Most duplexes are manufactured for 14 or 12 gauge wire, including the hospital grade receptacles that audiophiles often use. If you put a 10 gauge wire in it, the receptacle may overheat and pose a fire hazard if it's not rated for this size of wire. Or the wire won't fit properly in the receptacle. Either the screw on the side won't hold it and the wire will work itself loose with temperature changes, or the little hole at the back for inserting the wire directly into the duplex will be too small. So people may jam it in damaging it. It should say on the duplex itself what size wire you can use. Ten gauge wire is fine. I'm not disputing that. I'm just suggesting that people be careful to do it properly. Also keep in mind that there are often local electrical codes that add to the NEC, thereby imposing stricter requirements. You have to check the area where you live.
Dedicated power
After a lot of research and consideration, mostly between power conditioners and dedicated circuitry, I have decided to go with 3 dedicated lines. One for amp one for pre and a 3rd for CD or digital. What I'm thinking is that I can pull the wire myself and then hire a professional electrician to do the breaker work and wall terminations using hospital grade outlets. My question is what wire should I use? I have heard of people using 12-2 or 10-2 but don't have knowledge of wire specific details. Anybody up on this?
- ...