HELP I think I have an electrical issue??


A few months ago I had 2 20amp dedicated lines with hospital grade duplex's installed. All was well with my Bel Canto Ref1000 mono's. Well a few days ago I just got a pair of Genesis m60 tube amps. I was noticing a clicking noise coming through my speakers. I first noticed this when I was just warming up the amps with no source on. Then I also noticed the clicking when a source was on with music playing.

So it turns out that the clicking noise is my electric ignition of my gas furnace, is somehow playing through my speakers (Or maybe its just one of them, not exactly sure yet) This is a very strange and annoying. If anyone has any ideas please let me know!

Tim
tmesselt
The most fundamental difference between now and when the problem was not present, aside from the different amps, is that previously there were balanced connections, and now there are single-ended connections.

As Jim's "myths" link makes clear, the shields of single-ended interconnects, while serving as the return path for signals that are transmitted between the connected components, also conduct extraneous currents caused by ac ground differentials between the components (since the shields tie together the chassis of the components, which in turn are connected to both signal ground and ac safety ground). The common path causes coupling of ac-related noise into signal, since the receiving component has no way of distinguishing between the two. Balanced interfaces are a completely different story, and are essentially immune to this kind of effect.

So my first suggestion, if you have not already tried it, would be to connect EVERY component in the system to the SAME dedicated line, to minimize ground offsets between the components.

Beyond that, it IS very conceivable to me that a better quality interconnect would help, because it would presumably (although not necessarily) have lower shield resistance, which would tend to "short out" voltage offsets between the chassis of the connected components. As well as providing better immunity to airborne rfi.

Regards,
-- Al
First, ensure the pilot assembly and ignition module are grounded. The pilot can be grounded by using a double insulated or bare, solid copper wire from a mounting screw directly to the "GND" terminal on the module, if so equipped, otherwise to chasis. You can also ground the neutral side of the 24V transformer.

If that doesn't work, consider an isolation transformer.
Your best bet, do all the above! I've done everything but the balanced cable (too much SE equipment I love), clean AC is quite an advance in sonics.

Also, if not previously mentioned, make sure you have a good solid house ground.
If you put the previous amps back in place and the problem is gone I would blame the Genesis amps. Like I said, not necessarily that they are malfunctioning, but that they just don't filter out issues with your AC. Maybe they are just more susceptible to noise on the AC line.
I have had amps that showed quirks where others did not.
BTW, what did you do with the Ref1000s?
Hevac1,
Hospital grade receptacles do not have to be isolated ground type receptacles.

The ever so popular Hubbell HBL 8300H hospital grade duplex receptacle

Hubbell IG8300 hospital grade duplex receptacle.