For me I changed my 15 amp breaker to 20 amps because it popped occasionally on power up only, never while playing loud. I had 9.6kW output into 4 ohms though...
What is the branch circuit wiring size? If it’s #14awg cu the breaker, per electrical safety code, can not be larger than 15 amp. Solution is to install a 15 amp HM (High Magnetic) breaker. An HM breaker has a longer lag time for turn on high inrush current.
Here are three examples, of manufacturers HM breakers.
https://www.homedepot.com/p/Square-D-QO-15-Amp-High-Magnetic-Single-Pole-Circuit-Breaker-QO115HM/303...
https://www.widespreadsales.com/Products/Circuit-Breakers-Siemens/Q115HM
https://www.eaton.com/us/en-us/skuPage.BR115H.specifications.html
CH-HM Breakershttps://bse-assets.azureedge.net/ISSheet_117983.pdf
CH-HM breakers are designed with
high magnetic trip settings. Single-
and 2-pole CH-HM breakers (“HM”
suffix) rated 15 and 20 amperes are
recommended for circuits with
inherently high inrush currents.
.