I've got news for you. It is not just the breaker. 20 Amp services have larger diameter (smaller gauge) wire to support the additional current draw. Changing the breaker and not the wire is theoretically asking for a fire. Most amps in home situations are going to do fine on a 15 Amp service. You can't drive an amp at full continuous power. It will be distorting on peaks and will sound stressed long before you get there. Just 3 dB down is 1/2 power and you are probably still distorting peaks at this level. This is why power is so important. To avoid clipping peaks and sounding stressed your loudest listening level should be 1/10th peak power or if you like listening at an average power of 50 watts, you need an amplifier capable of 500 watt peaks. Depending on the efficiency of the loudspeakers most of us are only listening at an average power of 1 to 25 watts. The outlier here is class A amplifiers. They draw a lot more idling than other designs unless they have a bias adjusting scheme.
- ...
- 24 posts total
Look at the wattage on the back of the unit. So long as you don't exceed a combined 1500 watts you are fine.
The watts on the input and output are more or less the same, however because P = Current x Voltage, when you change the voltage (downwards) the Current may go upwards. That instant current capacity is not drawn from the outlet but from storage capacitors in the power supply. |
fiesta75632 posts@ fiesta75 What is the branch circuit wiring size? If it’s #14awg cu the breaker, per electrical safety code, can not be larger than 15 amp. Solution is to install a 15 amp HM (High Magnetic) breaker. An HM breaker has a longer lag time for turn on high inrush current. Here are three examples, of manufacturers HM breakers. https://www.homedepot.com/p/Square-D-QO-15-Amp-High-Magnetic-Single-Pole-Circuit-Breaker-QO115HM/303... https://www.widespreadsales.com/Products/Circuit-Breakers-Siemens/Q115HM https://www.eaton.com/us/en-us/skuPage.BR115H.specifications.html CH-HM Breakershttps://bse-assets.azureedge.net/ISSheet_117983.pdf . |
jea; I never, tripped the breaker, just don't want to put a strain on my amps. Like I wrote earlier, is that there’s 12/2 romex to a 15 amp rec. which is fine. I’m sure I can still change the breaker to 20 amps with 12/2, which should be code, & leave the 15 amp rec.. This is for my AV, I don’t think I use 1/4 of the max of power when watching a movie. Now when listening to music, sometimes I just jam. Different system. Thanks for you response! |
- 24 posts total