Why is it necessary to have gear on the same phase from electrical panel?


The source of power from any circuit is 120 V - therefore having some circuits on a different phase Side from the panel would seem OK.

It sounds nice to have everything on the same phase but does it really matter?

The only thing I can think of that would improve things is to keep all the noisy stuff on one side of the panel, like refrigerator, and the cleaner stuff on the other side.

jumia

The only thing I can think of that would improve things is to keep all the noisy stuff on one side of the panel, like refrigerator, and the cleaner stuff on the other side.

Its a myth... No such thing. IF the electrician did his job right and followed NEC as well as AHJ he balanced the 120V loads, within reason, as evenly as possibly on both Lines, legs, to the common neutral.

Also, FYI, Line 1 (L1), leg, and Line 2 (L2), leg, feed both sides of the circuit breakers in the electrical panel.

Example:

(L1) - - BRK 1 - - - - - - BRK 2 - - (L1)

(L2) - - BRK 3 - - - - - - BRK 4 - - (L2)

(L1) - - BRK 5 - - - - - - BRK 6 - - (L1)

(L2) - - BRK 7 - - - - - - BRK 8 - - (L2)

And so on down each side of the panel.

 

The source of power from any circuit is 120 V - therefore having some circuits on a different phase Side from the panel would seem OK.

When audio equipment is connected together by wire interconnects it is best practice to feed all 120V audio equipment, as well as video equipment, from the same Line, leg. Either from (L1) to neutral or (L2) to neutral, but not from both Lines. Example say a 120V preamp is fed from (L1) and a 120V power amp is fed from (L2) there is a 240V potential, voltage, between the two HOT conductors feeding the two pieces of equipment. With this wiring configuration there is a greater chance of noise, hum, from the system through the speakers.

When both pieces of equipment are feed from the same Line there is not any nominal difference of potential, voltage, between the Hot conductors feeding the two.

That’s the basics....

"Less than 300 microamps of ground loop current can cause hum as it flows in an unbalanced audio interconnect cable. However, harmonics of 60Hz that are generated from lighting dimmers or switch-mode power supplies sound like Buzzz mixed with a bit of Hummm and are more easily coupled by even smaller currents. Harmonics can add together when equipment is powered from different phases, so clearly there is an advantage to specifying same-phase electrical service to power the electronics systems in most cases....

Any leakage currents on the safety ground wires of split single phase load circuits fed by different phase legs will add together due to the 240V potential difference....

Power conditioners do not solve any of these common problems: Cross phase coupling (doubles hums & buzzes) .... What actually does solve them: Same phase power.

http://www.exactpower.com/elite/assets/pdfs/theTRUTH.pdf
 

 

(With big Monster mono Power amps the user may not have a choice and may have to feed them from both Lines. OR if money is no object a large VA rated single phase 240V to 120V isolation transformer can be used. Result one 120V Line... I worked with a member that has a single phase 240V to 120V 15KVA outdoor Pad Mount transformer that feeds a 120V only sub panel for his dedicated audio room.)

.

Correction.

I worked with a member that has a single phase 240V to 120V 15KVA outdoor Pad Mount transformer that feeds a 120V only sub panel for his dedicated audio room.)

That should read:

I worked with a member that has a single phase 240V to 120V 15KVA outdoor Pad Mount transformer that feeds a 120V only panel for his dedicated audio room.)

It is not a sub panel.

.

Jea48

This is a really awesome explanation thank you very much.

I guess a Cable connected between two components that happen to be plugged into different circuits effectively creates a bridge of power between the two phases, although add to a very low Energy level.  The components are likely designed in such a way to avoid impact due to this bridge.  
 

Existence of the bridge nevertheless is a source of interference because there is some communication between the two components of electricity flow which causes noise?  
 

Even if you use the same Circuit for connecting components and mixing outlets you still run the risk of creating hUms because use of different outlets causes ground loop issues because grounding is now shared between two outlets which is not healthy and creates an antenna along the grounding path. Does all this make sense?

This is my issue with both plugs in an audio room having to be on the same hot wire. One side is grounded anyways &neutral) Hotside is grounded thru an average of 10 ohms with other items connected in the house and your audio gear anyways. A fe volts difference in an unbalanced load across both ht wires amunts to about zero infle

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

One side the neutral is connected to ground not matter what circuit hot side you are using. The hot is actually grounded too thru about 10 ohms load with other items in the house drawing current besides your audio gear and lower with AC running. What's the difference in noise with both circuits on one side or split by both hots?

 

 

 

 

I am sorry the post I was typing above decided on its own to post before I was finished. This site is finicky.