but now you have another path which is participating in that current flow.
That is correct. I have been wondering if somehow the provided parallel path is what caused the GFCI to trip. My math above says 3mA. I doubt that was the reason the GFCI tripped. I’m not sure the 3mA number has an relevance to why it tripped.
Maybe it was the parallel path I provided... I apparently upset the sensing unit in the GFCI though.
.
I’d be curious to see you measure the actual current next time. :)
I have been thinking about that myself. I think a resistance should be put in series with the amp meter. That would replicate a small ground fault leakage more like that of a piece of equipment.
I keep going back to your statement in a post above.
GFCI outlets do go bad, but it could also be equipment with a leaky capacitor to ground
I don’t know how old the OP’s equipment is but I believe some equipment manufacturers put a cap or sometimes a high ohm-age resistor connected from the neutral to the chassis. If it is a leaky cap would it be more susceptible to pass current to the chassis at 60V potential to ground than a few millivolts to ground? (Equitech 1.5Q AC mains Conductor that feeds the neutral wire in the equipment is ungrounded 60V to ground.) (House wiring branch circuit neutral conductor a few millivolts to ground at the chassis.)
All conjecture on my part though.
.